No, that's not what I meant. Of course you need the noout flag, that's the first point on the list I sent. Other flags are not required as pointed out by croit. I have never disabled cephfs before shutting it down as mentioned by Gerard, so I can't comment on that. The procedure I quoted from SUSE is still working fine, that's how we power off our (cephadm) based clusters as well. Zitat von gagan tiwari <gagan.tiwari@mathisys-india.com>:
Hi Eugen, I had deployed the cluster via cephadm. so, it's container based. Just fyi..
So, you meant I don't need to run any commands like "ceph osd set noout" , "ceph orch stop osd.<ID>" ,etc.
I just need to power off all nodes starting clients nodes , osd nodes , mon , mds nodes and power them on after maintenance activity is over.
Thanks, Gagan
On Wed, Aug 6, 2025 at 11:53 PM Eugen Block <eblock@nde.ag> wrote:
You don't need to stop all the OSDs (or other daemons) manually, just shut down the servers (most likely you have services colocated). When they boot again, the Ceph daemons will also start automatically (they're handled by systemd). I can check tomorrow which steps exactly our shutdown procedure consists of when we have planned power outages etc.
Zitat von gagan tiwari <gagan.tiwari@mathisys-india.com>:
HI Eugen, We have 80 osds in the cluster.
So, to stop them I will need to run the command *ceph orch stop osd.<ID>* for all 80 osds one by one. Is there any way to stop all of them in one command ?
Also, once all nodes will be back after power maintenance activity , will I need to start all daemons mon , mds , osd,etc ? or will they be up automatically once servers will be up ?
Thanks, Gagan
On Wed, Aug 6, 2025 at 4:45 PM Eugen Block <eblock@nde.ag> wrote:
Although SUSE discontinued their product, the procedure is still correct [0]:
1. Tell the Ceph cluster not to mark OSDs as out:
ceph osd set noout
2. Stop daemons and nodes in the following order:
Storage clients
Gateways, for example NFS Ganesha or Object Gateway
Metadata Server
Ceph OSD
Ceph Manager
Ceph Monitor
3. If required, perform maintenance tasks.
4. Start the nodes and servers in the reverse order of the shutdown process:
Ceph Monitor
Ceph Manager
Ceph OSD
Metadata Server
Gateways, for example NFS Ganesha or Object Gateway
Storage clients
5. Remove the noout flag:
ceph osd unset noout
[0]
https://documentation.suse.com/en-us/ses/7.1/html/ses-all/storage-salt-clust...
Zitat von gagan tiwari <gagan.tiwari@mathisys-india.com>:
Hi Guys, I have recently set-up a production ceph cluster
which
consists of 3 monitor nodes and 7 Osd nodes.
There is power maintenance activity scheduled at the data centre coming weekend and due to that I need to power off all the devices.
Can you please advise me on the safest way to power off all servers?
Should I power off all 7 OSD servers one by one followed by all 3 monitor nodes or vice versa?
Thanks, Gagan _______________________________________________ ceph-users mailing list -- ceph-users@ceph.io To unsubscribe send an email to ceph-users-leave@ceph.io